Hello Fellow Wizards,
I have a couple of troubleshooting related questions in a paramedical environment.
PROLOGUE: Client called due to hearing a "Buzzing Sound," during normal operational hours, from a utility room that houses all the load centers, electrical enclosures, disco's and pull-boxes.
While this "Buzzing Sound" occurred, client noted that it did NOT have any negative impact to their medical tools, dedicated medical equipment, lighting, outlets or phone systems.
When i arrived to inspect and troubleshoot noise, the manager on shift stated that the "Buzzing Sound" had randomly stopped (however, we all know that these type of problems rarely if ever resolve on their own, especially when they create a "Buzzing Sound" from any electrical enclosure). So the next thing i did was the following:
A. Took note of all medical equipment in continuous use during normal work hours
B. Panel these circuits and breakers are on are labeled as follows: [ Siemens P1 Panel ][ 250A Max ] | [208/120V 3Phase] installed on May 2022. Breakers are of SiemensType HBL / IAC Rating 65KA / HACR Type SWD, 40'C
B1. Total of (4x 20A SP and x1 DP 20A, all #12AWG5 stationary medical appliances/equipment that were used for 3 or more hours which are listed below:
B2. Next step was to open panel that housed all medical equipment and appliances. After inspection i noticed that 6 circuits had conductors AND breakers that were noticeably warmer than normal, like hot hot to the touch (unfortunately did not have my therm-cam) with a DP breaker (2 out of the 6) was substantially hotter than the other 4 breakers.
//
//
QUESTION(S): My question is as follows:
A. Is it safe to say that "Buzzing Sound" was not a short or a ground fault, but the actual breaker(s) malfunctioning due to the continuous use of the medical equipment described above ?
B. If (A) assertion is erroneous, then what else could cause the "Buzzing Sound" ? (which was made from Utility Room that housed panels, discos and pillboxes)
C. if (A) assertion is agreed upon by majority consensus of wizards. then can i upsize these specific 6 circuits from 20A -> 30A and #12 - > #10AWG ?
Thank you for taking the time to read my question(s), i appreciate all your help and wisdom oh great council of Sages, Priests and Wizards.
I have a couple of troubleshooting related questions in a paramedical environment.
PROLOGUE: Client called due to hearing a "Buzzing Sound," during normal operational hours, from a utility room that houses all the load centers, electrical enclosures, disco's and pull-boxes.
While this "Buzzing Sound" occurred, client noted that it did NOT have any negative impact to their medical tools, dedicated medical equipment, lighting, outlets or phone systems.
When i arrived to inspect and troubleshoot noise, the manager on shift stated that the "Buzzing Sound" had randomly stopped (however, we all know that these type of problems rarely if ever resolve on their own, especially when they create a "Buzzing Sound" from any electrical enclosure). So the next thing i did was the following:
A. Took note of all medical equipment in continuous use during normal work hours
B. Panel these circuits and breakers are on are labeled as follows: [ Siemens P1 Panel ][ 250A Max ] | [208/120V 3Phase] installed on May 2022. Breakers are of SiemensType HBL / IAC Rating 65KA / HACR Type SWD, 40'C
B1. Total of (4x 20A SP and x1 DP 20A, all #12AWG5 stationary medical appliances/equipment that were used for 3 or more hours which are listed below:
- Boilers (x3) plugged into 20A gfi on dedicated circuit | 3.5-4.5 hours of continuous
- Vacuum System DP20A on dedicated circuit and has its own disco next to it with step down transformer | 8 - 9.5 hours of continuous use
- Duplicator SP 20A plugged into 20A gfi on dedicated circuit | 24/7 hours of continuous
B2. Next step was to open panel that housed all medical equipment and appliances. After inspection i noticed that 6 circuits had conductors AND breakers that were noticeably warmer than normal, like hot hot to the touch (unfortunately did not have my therm-cam) with a DP breaker (2 out of the 6) was substantially hotter than the other 4 breakers.
//
//
QUESTION(S): My question is as follows:
A. Is it safe to say that "Buzzing Sound" was not a short or a ground fault, but the actual breaker(s) malfunctioning due to the continuous use of the medical equipment described above ?
B. If (A) assertion is erroneous, then what else could cause the "Buzzing Sound" ? (which was made from Utility Room that housed panels, discos and pillboxes)
C. if (A) assertion is agreed upon by majority consensus of wizards. then can i upsize these specific 6 circuits from 20A -> 30A and #12 - > #10AWG ?
Thank you for taking the time to read my question(s), i appreciate all your help and wisdom oh great council of Sages, Priests and Wizards.