BX sheathing reuse to house THHN
Fred B
Upstate, NY
I have a residential job with a highly finished ceiling that has a bad and VERY old BX powering a light fixture. Question is "IF" old wire can be pulled out of the BX, can I reuse the sheathing and pull in new THHN to provide power for light fixture and not damage the ceiling? Any NEC requirement that would prohibit this?
Short answer no. Type AC cable is a cable assembly that as the conductors installed during the manufacturing process. The sheath is not listed to be used as a raceway so the sheath would need to be listed as FMC to be used as you've described.
What was BX listed as
I've encountered very old BX with cloth and rubber insulation, where the conductors were over wrapped with cloth, where the conductors could be easily pulled out. The overall diameter was larger than modern BX as well.
Doesn't really change that the sheath is not suitable for new conductors.
Jon
The ironic part of this question is that if you could pull out the old conductors and replace them with THHN the wiring would be much safer than leaving the old junk. :sneaky:
One other point: where I've encountered similarly really old BX, it was often fished into walls rather than new construction. Bit is very likely that this old cable could simply be pulled out while pulling in a complete new cable.
Also, note that cable assemblies are installed in a different fashion than raceways. You can have lots of bends in a cable assembly but not in a raceway.