Suitable in the sense of recognized for use as an EGC, at the time it was sold, by NEC and UL, not necessarily deserving that recognition in hindsight....Although the "newer" stuff after about 1953 contained the bonding strip the cable that predated that was still suitable for use as an EGC.
I would treat the same way you would approach reduced sized EGC's in NM cable.
I would treat the same way you would approach reduced sized EGC's in NM cable.
How to treat reduced sized egc in nm. Never knew there was a way to treat them.
As far as the old bx that the sheath isn't considered ground. It is ground (or bonded) so would 406.4 (D) (1) apply? or no because of the "no" strip?
Just do not try to use the sheath as a current carrying conductor. :lol:I think Infinity is saying you treat the NM cable with smaller EGC the same way as you treat regular NM cable.
Just treat the old BX cable as a regular BX cable. I am sure if it sees a fault current the breaker will respond.
I would say only if it was recalled, which apparently it was not.I know of no document that says that an AC or NM cable that was code complaint when installed is suddenly not code compliant.
I think Infinity is saying you treat the NM cable with smaller EGC the same way as you treat regular NM cable.
Just treat the old BX cable as a regular BX cable. I am sure if it sees a fault current the breaker will respond.
I think the meaning there was, consider the fact it once was compliant, now it isn't, but the existing is technically still compliant. If you have something existing proceed with caution. Leaving it in place is not necessarily wrong, extending it is not so clear as to whether it is right or wrong.Think I got it.
There is nothing. No article.
Treat it as a egc. The way I've been treating it.
Even the older bx.
Correct?
I think Infinity is saying you treat the NM cable with smaller EGC the same way as you treat regular NM cable.
Just treat the old BX cable as a regular BX cable. I am sure if it sees a fault current the breaker will respond.
Maybe I'm wrong, but my understanding is that I am not allowed to extend an existing circuit run with NM cable with reduced size EGC.
Then again, you can always protect the circuit by a GFCI if it comes down to "you can not extend a circuit with an undersized EGC"