Toros
- Tujunga, CA
hi
Where Do I get C & Z-value of copper for 3 phase voltage drop calc???
Thank you
Thank you
hi
Thank you
My dear wife does it all the time..........Anyone ever feel like you are talking to yourself?![]()
not an issue
now answering is another matter
"If I wanted your opinion, dear, I would have told you what it is."My dear wife does it all the time..........
Maybe the OP will explain what C he is referring to.
For voltage drop one would normally refer to R and Z.
But what would I know - I'm just thick according to..................you know who.
What does the c-value mean here
Area of a conductor, circular mils ???
see attached
Thank you
Ed:happysad:
not an issue
A lot of that happens. Here and elsewhere. It irks me too (or two or to) but I try to let it go under the radar as long as the intended meaning is clear. There are bigger things to worry about.Did anyone else notice that they spelled “fault” incorrectly on that chart? My brain can’t avoid seeing things like that, sometimes I get tired of it because I get stuck on it.
thank you,TOROS
Refer to page 6 of 10 on LINK provided by "JUMPER".
C - constant values used in the Point-to-Point calculation method.
PDF has ALL the formulas used depending on 3P-1P-etc.
Keep a copy, you can put the formulas into a spreadsheet and calc your own results as needed.
The VD drop calcs on the PDF you provided I believe are incorrect.
Listing a Z value from Chap 9-Table 9, which is calculated at PF=0.85.
Formula on PDF seems to be adding another factor of 0.8...not sure where this is coming from.
Z values in your PDF tables are NOT the Z values from NEC except for the #4/0.
That chart is not VD.The bottom one is.
No, C there is some constant (non-changing variable) used for a short circuit calculation, Isc.
I have no clue what it stands for or how it is derived. It is not total circular mils however.
That is an EE level calc for the most part, I have never did it.
Here is a good link with math and charts if you are interested.
http://www.cooperindustries.com/con...rary/BUS_Ele_Tech_Lib_Electrical_Formulas.pdf
imho that method is confusing and more complicated than necessary
just do a single line with the Z for each xfmr/wire segment
can be modified from infinite bus to util supplied values by reflecting util Z to sec
easy to make an excel spreadsheet