C1/D1 Keyosk & Art. 514

Status
Not open for further replies.

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Since Article 514 is the ruling text, the answer is NO.

See Diagram 514.3. The kiosk mentioned in the OP would be within the 18? high, 20? radius, Division 2 location.

In many applications general purpose equipment would be acceptable, but Section 514.7 directs you to Section 511.7 which would prohibit most of the kiosk wiring and equipment.
 
Status
Not open for further replies.
Top