Question came to me on the following:
"We have a Class 1 Div 1 sewer wet well with 4 GRC raceway's leaving it going into another vault where we have the seal-off's, it changes from GRC to PVC at that point and then still under ground stubs up to our control panel. For the Bonding question, the contractor I am talking about ran a 1 inch pvc pipe from the control panel underground to the seal off vault and bonded to the 4 raceways. Do the GRC raceways have to be bonded at both end or is one fine and does this sound like an appropriate installation to you?? "
My answer:
The NEC requires the electrical continuity of the ...raceways in hazardous locations to be per the methods in 250.92(B)(2) to B 4 and essentially this means RMC from the haz location to the source. See 250.100 The method the contractor used does not comply with 250.100. The 2005 NEC clarified that even with a supplemental EGC, the bonding in 250.92 is required.
Whats the opinion of the forum? The AHJ says the installation is OK.
"We have a Class 1 Div 1 sewer wet well with 4 GRC raceway's leaving it going into another vault where we have the seal-off's, it changes from GRC to PVC at that point and then still under ground stubs up to our control panel. For the Bonding question, the contractor I am talking about ran a 1 inch pvc pipe from the control panel underground to the seal off vault and bonded to the 4 raceways. Do the GRC raceways have to be bonded at both end or is one fine and does this sound like an appropriate installation to you?? "
My answer:
The NEC requires the electrical continuity of the ...raceways in hazardous locations to be per the methods in 250.92(B)(2) to B 4 and essentially this means RMC from the haz location to the source. See 250.100 The method the contractor used does not comply with 250.100. The 2005 NEC clarified that even with a supplemental EGC, the bonding in 250.92 is required.
Whats the opinion of the forum? The AHJ says the installation is OK.