Okay, so we're installing an air compressor in a Class 1, Div II, Group D haz location. The air comp comes in an enclosure that includes a soft starter, PLC, motor, and all related switches and transmitters to go to the PLC. We were recommended to do a Z-purge on the enclosure (NEMA 4X), but the Z-purge will be only over the motor starter part of the enclosure, and apparently the vendor is saying th PLC is already rated for Div II, but i think they only meant the outside control panel.
The motor shouldn't be a problem from what I read in the NEC since it is a brushless rotary screw compressor. My main concern is that the PLC uses a temperature switch, pressure switch, and differential pressure switch as well as various pressure transmitters and temp sensors, fuses, relays and contacts that go to the enclosed PLC.
Do all of the switches, transmitters, and PLC parts need to be rated for Div II as well since apparently the Z-purge is only covering the motor starter portion of the enclosure? Or since they are all enclosed in the 4X enclosure is that good enough? Do they need to be NEMA 7 or explosion proof rated?
The motor shouldn't be a problem from what I read in the NEC since it is a brushless rotary screw compressor. My main concern is that the PLC uses a temperature switch, pressure switch, and differential pressure switch as well as various pressure transmitters and temp sensors, fuses, relays and contacts that go to the enclosed PLC.
Do all of the switches, transmitters, and PLC parts need to be rated for Div II as well since apparently the Z-purge is only covering the motor starter portion of the enclosure? Or since they are all enclosed in the 4X enclosure is that good enough? Do they need to be NEMA 7 or explosion proof rated?