cdcabrera
Member
- Location
- Riverside, CA
I have a customer mixing and matching NEC and IEC and the sales guy agreed to the technical clarifications that support this conflict. Everything I have read in the code book, checked with vendors, and such indicates I am about to open a can of worms and want to be prepared as possible.
C1, D2, Gr B, T3 is the area classification that I was given for the project. Customer has opted for IS wiring, my responsibility is to get signals to the edge of the my package in a JB, so they are handling all the hard work.
JB just has TBs in it, so simple devices.
The local control panel will have PL, PB, HOA, HMI, ethernet switch, and power supplies will be purged, so I don't believe additional the a
I got my Panel Layout drawings back with the comment
"Ensure JB is complying with Nema 4x and C1,Div2,Group B,C,D T3 with Ex-d"
Based on 504.10(C) the JB does not need additional safety ratings since there are simple devices. 500.7(D) solves the problem for the LCP.
Is there something I am missing in my considerations? If i am going to to NEC and explosion proof then I get to step up to NEMA 7 enclosure which I am trying to do.
C1, D2, Gr B, T3 is the area classification that I was given for the project. Customer has opted for IS wiring, my responsibility is to get signals to the edge of the my package in a JB, so they are handling all the hard work.
JB just has TBs in it, so simple devices.
The local control panel will have PL, PB, HOA, HMI, ethernet switch, and power supplies will be purged, so I don't believe additional the a
I got my Panel Layout drawings back with the comment
"Ensure JB is complying with Nema 4x and C1,Div2,Group B,C,D T3 with Ex-d"
Based on 504.10(C) the JB does not need additional safety ratings since there are simple devices. 500.7(D) solves the problem for the LCP.
Is there something I am missing in my considerations? If i am going to to NEC and explosion proof then I get to step up to NEMA 7 enclosure which I am trying to do.