I have been working on a sewer wet well installation. The wet well is defined as class 1 div 1 by NFPA820. The submersible pumps have a multiconductor cord that is sealed into the pump and extends from the wet well to a JB where it is terminated. This cord passes through a pipe, sleeve, conduit, whatever you want to call it that stops at grade level and is not sealed. The cable extends upward into an enclosure that has a class 1 div 2 cable gland fitting installed. This JB is mounted greater than 3 feet above the open pipe that passes into the well. From the JB we have rigid conduit with poured seal off fittings running to the MCP that is located greater than 5 feet from any well openings.
In my opinion the open pipe from the well, C1D1, extends that C1D1 classification to the opening of the pipe and as long as the boundary distances are met and we do not intend on extending the pipe outside of the boundary area, a poured seal off is not required. It is only required if we want to stop the C1D1 boundary distance.
According to NFPA820, 3 feet beyond any opening into the well is C1D1. Between 3 feet and 5 feet is C1D2 and beyond 5 feet is unclassified.
This has been a very long topic of discussion, and I would really like some input.
In my opinion the open pipe from the well, C1D1, extends that C1D1 classification to the opening of the pipe and as long as the boundary distances are met and we do not intend on extending the pipe outside of the boundary area, a poured seal off is not required. It is only required if we want to stop the C1D1 boundary distance.
According to NFPA820, 3 feet beyond any opening into the well is C1D1. Between 3 feet and 5 feet is C1D2 and beyond 5 feet is unclassified.
This has been a very long topic of discussion, and I would really like some input.