I have a new plant that is trying to figure out how to satisfy the VFD needs, Temperature switches for surface ignition and field disconnects. Sorry that was a run in sentence.
We are going to use Allen Bradley Powerflex 525. AB says that the control circuit and power needs to be in separate conduits. The electrician said that motors only have 1 conduit inlet. We can't use Intrinsically safe inputs because we can't keep 2" separation in the pecker head.
Is there a code requirement for auxiliary contacts on field disconnects when using VFDs? I have seen a boatload of different installations where guys use 480vac and 24vdc in the same pipe for the field disconnect. Then the next contractor does 2 pipes. The next contractor uses VFD cabme with 2 control wires for the AUX. One old school contractor put relays in the panel so he could run 120 VAC with the 480 VAC in 1 pipe then have the relay control the 24VDC.
I haven't found any code requirement and it's probably one of the we've always done it this way answers. I'm the controls guy and we are just doing panels and start up. No pipe &wire or terminations.