i am packaging a pump system for customer with their supplied instrumentation.
the area classification is c1, d2, group c/d per the supplied documentation.
the sticky situation is they have supplied a level switch that is c1, d1 rated. i have added a rated elbow and seal directly out of the switch, isolating it from the rest of conduit run. this installation should satisfy 501.10 (A) 501.15(A) and 501.15 (4).
am i missing something?