Al Pike
Member
- Location
- Honesdale, Pa
I have a C1D2 classification for a pump station of 18''above and 3' from the station edge.
Question,as long as I'm above the 18'' and my conduits conform to 501.15(b)(2)exception 1, I would not need a seal even though I'm within 2' of the station edge if I install my trough at a height of 30''.
Ex:conduit that contains no unions,couplings,boxes,or fittings,and passes completely through a C1D2 with no fittings less that 12'' beyond the boundry shall not be required to be sealed.
Thanks,I'm just making sure I'm correct.
Question,as long as I'm above the 18'' and my conduits conform to 501.15(b)(2)exception 1, I would not need a seal even though I'm within 2' of the station edge if I install my trough at a height of 30''.
Ex:conduit that contains no unions,couplings,boxes,or fittings,and passes completely through a C1D2 with no fittings less that 12'' beyond the boundry shall not be required to be sealed.
Thanks,I'm just making sure I'm correct.