Can the cabinet be the only bond between 2 ground bars or must there be a bonding jumper between the 2 bars? Factory installed bars. Metered between the 2 an got 0.01 ohms.
No jumper is required. This has always been the case but in the 2020 NEC new language was added as 250.109 to make this clear.Can the cabinet be the only bond between 2 ground bars or must there be a bonding jumper between the 2 bars? Factory installed bars. Metered between the 2 an got 0.01 ohms.
I agree even without the new language.No jumper is required. This has always been the case but in the 2020 NEC new language was added as 250.109 to make this clear.