RichB
Senior Member
- Location
- Tacoma, Wa
- Occupation
- Electrician/Electrical Inspector
Morning everybody,
I need you to help me out again,,,
We have several cabinets that have a gasketed, removable panel that our contractor brought his conduits thru.
He did not use a grounding bushing on the conduit, the bolts that hold the panel on do not cut through the paint and the lock nuts do not cut the paint to what we ( myself andf the other inspectors) would consider enough to be used as a bond.
So, we feel that there is NOT a bond between the conduit, panel and the rest of the system. We are asking for a bonding bushing and a jumper, and the contractor is saying no.
I know I have seen something, either in the Bonding/Grounding class or read it in the NEC but casn't find it and I don't have enough hair left to keep tearing out!!LOL
My question is--do any of you have a reference for requireing how the removable panel and conduit are to be bonded?
Thanks again folks!!
Rich
I need you to help me out again,,,
We have several cabinets that have a gasketed, removable panel that our contractor brought his conduits thru.
He did not use a grounding bushing on the conduit, the bolts that hold the panel on do not cut through the paint and the lock nuts do not cut the paint to what we ( myself andf the other inspectors) would consider enough to be used as a bond.
So, we feel that there is NOT a bond between the conduit, panel and the rest of the system. We are asking for a bonding bushing and a jumper, and the contractor is saying no.
I know I have seen something, either in the Bonding/Grounding class or read it in the NEC but casn't find it and I don't have enough hair left to keep tearing out!!LOL
My question is--do any of you have a reference for requireing how the removable panel and conduit are to be bonded?
Thanks again folks!!
Rich