Apologies in advance for the lengthy post.
I am looking for recommendations from my fellow consulting colleagues regarding a situation that recently came to my attention while reviewing a client?s wiring documentation.
My client is in the elevator industry, and like virtually all companies in this trade, uses flexible multi-conductor ?travel cables? to provide communications, control, signaling and power between the machine (control) room and the moving elevator car. NEC Article 620 governs details for elevators; however, because nothing is specifically identified in 620, I?m left to rely on Article 725 (Class 1 circuitry) and Articles 310 & 400 for guidance regarding proper ampacity adjustment of the individual conductors in the travel cable.
A typical elevator travel cable has three (or possibly more) different types of circuits:
1. ?Lighting circuit(s)? ? Provides power for in-car (passengers) and car-top (service) lighting, in-car ventilator, and in-car and car-top outlets. The in-car lighting and ventilator are considered continuous use, while the others are typically intermittent/non-continuous loads. There are typically <1 dozen conductors of this type in the travel cable.
2. ?Safety and control circuits? (Class 1): typically ~3 dozen conductors of this type in the travel cable.
3. ?Signaling and communications circuits? (Class 1): typically ~2 dozen conductors of this type in the travel cable.
I am particularly concerned about the typical 20A circuit breaker rating vs. the derated conductor ampacities for the typical ?lighting circuit? conductors in the travel cable.
Several of my client?s electrical engineers (employees) believe that the 12AWG lighting circuit conductors can be protected by a 20A breaker regardless of the number of conductors in the travel cable (or any additional considerations). I disagree, pointing to the following adjustment contributors:
1. Number of current-carrying conductors in the cable,
2. Temperature rating of the conductor insulation (60C),
3. Minimum temperature rating of the terminals that the conductors are wired to (60C), and
4. Maximum ambient temperature (40C).
There is some debate between one of the engineers and myself as to which conductors must be considered ?current carrying?. My understanding, per NEC Article 725.28 (B), is that any of the Class 1 conductors carrying more than 10% of their temperature-adjusted ampacities are considered to be current carrying, and must therefore be included when calculating the adjustment factor in Table 310.15 (B)(2)(a).
Let?s determine the maximum OCPD ratings for each of the circuit conductors. As a hypothetical exercise, let?s assume the following to make sure that everything is being calculated correctly:
1. 6 lighting circuit conductors, 12AWG each; all can be considered current carrying.
2. 3 equipment grounding conductors, 12AWG; none are considered current carrying.
3. 32 safety and control conductors, 16AWG each; Based upon NEC 725.28(B), 75% can be considered current carrying.
4. 22 signaling and communications conductors, 20AWG each; none will be considered current carrying. (typically <10mA each).
In this example, we have (6 x 100%) + (32 * 75%) = 30 current-carrying conductors in the travel cable. Based upon my calculations, the maximum allowable continuous load on each 12AWG lighting circuit conductor is ~9.2 Amperes, with a maximum end-to-end length of ~100 feet for less than 3% voltage drop. It seems clear to me that you wouldn?t protect these lighting circuit conductors with 20A circuit breakers.
I am recommending that the client install inline 12A fuse between the 20A circuit breaker(s) and the travel cable 12AWG lighting circuit conductors. Do you agree? If not, why? What am I missing?
Thanks,
Jeff
I am looking for recommendations from my fellow consulting colleagues regarding a situation that recently came to my attention while reviewing a client?s wiring documentation.
My client is in the elevator industry, and like virtually all companies in this trade, uses flexible multi-conductor ?travel cables? to provide communications, control, signaling and power between the machine (control) room and the moving elevator car. NEC Article 620 governs details for elevators; however, because nothing is specifically identified in 620, I?m left to rely on Article 725 (Class 1 circuitry) and Articles 310 & 400 for guidance regarding proper ampacity adjustment of the individual conductors in the travel cable.
A typical elevator travel cable has three (or possibly more) different types of circuits:
1. ?Lighting circuit(s)? ? Provides power for in-car (passengers) and car-top (service) lighting, in-car ventilator, and in-car and car-top outlets. The in-car lighting and ventilator are considered continuous use, while the others are typically intermittent/non-continuous loads. There are typically <1 dozen conductors of this type in the travel cable.
2. ?Safety and control circuits? (Class 1): typically ~3 dozen conductors of this type in the travel cable.
3. ?Signaling and communications circuits? (Class 1): typically ~2 dozen conductors of this type in the travel cable.
I am particularly concerned about the typical 20A circuit breaker rating vs. the derated conductor ampacities for the typical ?lighting circuit? conductors in the travel cable.
Several of my client?s electrical engineers (employees) believe that the 12AWG lighting circuit conductors can be protected by a 20A breaker regardless of the number of conductors in the travel cable (or any additional considerations). I disagree, pointing to the following adjustment contributors:
1. Number of current-carrying conductors in the cable,
2. Temperature rating of the conductor insulation (60C),
3. Minimum temperature rating of the terminals that the conductors are wired to (60C), and
4. Maximum ambient temperature (40C).
There is some debate between one of the engineers and myself as to which conductors must be considered ?current carrying?. My understanding, per NEC Article 725.28 (B), is that any of the Class 1 conductors carrying more than 10% of their temperature-adjusted ampacities are considered to be current carrying, and must therefore be included when calculating the adjustment factor in Table 310.15 (B)(2)(a).
Let?s determine the maximum OCPD ratings for each of the circuit conductors. As a hypothetical exercise, let?s assume the following to make sure that everything is being calculated correctly:
1. 6 lighting circuit conductors, 12AWG each; all can be considered current carrying.
2. 3 equipment grounding conductors, 12AWG; none are considered current carrying.
3. 32 safety and control conductors, 16AWG each; Based upon NEC 725.28(B), 75% can be considered current carrying.
4. 22 signaling and communications conductors, 20AWG each; none will be considered current carrying. (typically <10mA each).
In this example, we have (6 x 100%) + (32 * 75%) = 30 current-carrying conductors in the travel cable. Based upon my calculations, the maximum allowable continuous load on each 12AWG lighting circuit conductor is ~9.2 Amperes, with a maximum end-to-end length of ~100 feet for less than 3% voltage drop. It seems clear to me that you wouldn?t protect these lighting circuit conductors with 20A circuit breakers.
I am recommending that the client install inline 12A fuse between the 20A circuit breaker(s) and the travel cable 12AWG lighting circuit conductors. Do you agree? If not, why? What am I missing?
Thanks,
Jeff