Hello...

Can someone please tell me which ampacity table should I be using for 5-wire single
insulated conductor in a conduit. Is it correct to refer to the Table B.310.1 (NEC 2008)?

Thank You!!
 
Hello...

Can someone please tell me which ampacity table should I be using for 5-wire single
insulated conductor in a conduit. Is it correct to refer to the Table B.310.1 (NEC 2008)?

Thank You!!
You can only use the tables in Annex B under engineering supervision.
This informative annex provides application information for ampacities calculated under engineering supervision.
 