Does the code allow NM Cable to bundled parallel through holes and along framing members.I saw this in Atlanta on residential wood framing and I have always done the one wire per hole and one wire per staple. I would assume that if this is allowed you would have to Derate the wire. Is it allowed with steel studs?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: cable bundling

In Washington State our electrical inspection agency only allows three NM cables per bored hole.
 