i was rejected today for having two romex wires entering a cable knock out in a 2-g box. 315.17(C) states messenger supported wiring, open wiring on insulators, and concealed knob and tube wiring, the conductors shall enter the box through individual holes. then the exception talks about clamps on single gang boxes and in a seperate sentance states multiple cable entries shall be permitted in a single cable knockout opening. why would it be allowed in a single gang box and not a 2-g or bigger? i see no difference in these boxes. the three methods specifically forbidden are single conductor systems, and that makes sense to me to use seperate holes for them. do i have a valid argument of should i just let it slid. thats a lot of work to fix this.