i am trying to figure out what options are available for cable entries into transmitter TE and moter on an NEC project.
This product is in class I DIV.2 GROUP B area.
can i use the 'Cord and cable fittings' type products such as Cooper Crouse Hinds CGB product[FONT=??]for the transmitter TE and moter cable entry.[/FONT]
 
Assuming both the enclosure and the cable are already suitable for Class I, Division 2, the fitting will depend on whether the enclosure is required to be explosionproof or not and the cable is armored or not.

The most generally applicable fitting would be similar to a type TMCX; it could be used in any scenario. A type similar to a CGB could only be used where the cable is NOT armored AND the enclosure is NOT required to be explosionproof. Note, in some cases an explosionproof enclosure may be used but may not be required to be.
 