Hello, one of my clients would like to use cable glands for the cable exits of their cabinet. According to my UL508A inspector, it is possible to integrate them if the cable gland is QCRV. Does this contradict the NEC? Thanks in advance.
Welcome to the forum. That sounds correct.Hello, one of my clients would like to use cable glands for the cable exits of their cabinet. According to my UL508A inspector, it is possible to integrate them if the cable gland is QCRV. Does this contradict the NEC? Thanks in advance.
Ul508a does not care as long as the holes are sealed with something that has the same environmental rating as the enclosureWelcome to the forum. That sounds correct.
What type of cable is it? Tray cable? and what voltage?
Does this contradict the NEC?
The nec does not much care about what is found in a listed assembly.Hello, one of my clients would like to use cable glands for the cable exits of their cabinet. According to my UL508A inspector, it is possible to integrate them if the cable gland is QCRV. Does this contradict the NEC? Thanks in advance.
What about it makes you think it might?Does this contradict the NEC?
Just because the code might not permit you to wire up to a UL 508a listed box with cord does not mean you can't install cord glands in the box.Thanks you for all your responses. As Tortuga says, I am from France, and some questions might seem strange to an American engineer.
In a documentation that UL had sent me, it was mentioned that "cable glands are not be suitable for fixed equipment. The NEC, Sections 400.7 and 400.8 does mentioned the permitted and not permitted uses. That's why i'm asking my initial question.