Can't see anything from that small picture.
-Hal
There is no requirement that the communications utility use the intersystem bonding point that the electrician is required to install.
Small examples of why telecom installers should not have "baby" exams. Their test questions ask things like What color is the green screw that you connect the ground to? They are taught you need to know chapter 7 and ignore 1-6.
Look at the mess of coax everywhere in the photo. Everyone else would get a fail from the inspector on neatness alone. If we just took anger bits and arbitrarily drilled holes through exterior walls we'd get a big fail on whichever Code applies. And half of them don't even put a box on the other end. Fail, fail, fail.
Perhaps that's the problem. Let them pull permits and see h9w quickly practices change.
Sent from my SM-T350 using Tapatalk
So you are saying they are not required to follow the NEC.
800.100,810.21,820.100,830.100 uses the words "shall be" Then 90.5 must apply.
Except the telecom utilities are not under the scope of the NEC. NEC does not apply until the customer side of the demark.
Same as for service drops, NEC does not apply ahead of the service point.
See 90.2 and the IN at the end.
...
They are utilities and not subject to the rules in the NEC. 90.2(B)(4)So you are saying they are not required to follow the NEC.
800.100,810.21,820.100,830.100 uses the words "shall be" Then 90.5 must apply.
They are utilities and not subject to the rules in the NEC. 90.2(B)(4)
That's not what NEC says.They are utilities and not subject to the rules in the NEC. 90.2(B)(4)
Hey, I'm not saying I don't agree with you 100% but if an AHJ had to inspect every cable, telephone or sat install there wouldn't be enough inspectors in the state or time in a year to do it. So I really don't think they even care. They have bigger fish to fry.
-Hal
We install the bonding bridge for them, not us but if we don't then we will get a call from the AHJHey, I'm not saying I don't agree with you 100% but if an AHJ had to inspect every cable, telephone or sat install there wouldn't be enough inspectors in the state or time in a year to do it. So I really don't think they even care. They have bigger fish to fry.
-Hal