DCThe differences should be small. Conductor temperature assumed will have the most impact on resistance. If you look on the "Specification 2" tab of the EasyPower data, it will show the "Field Temperature of Conductor". I think the default is 75 deg C and SKM uses 90 deg C.
EasyPower also has options for conductor lay and spacing that will also change the reactance. The insulation thickness used will also impact the reactance. You can open the EasyPower library to see all of the factors at play in the cable data. It's one of the most complicated parts of the EasyPower model. I would trust EasyPower more than SKM, but I'm biased because I used to work for EasyPower. But I've used SKM as well.
I would not expect any major differences in short circuit calculations or power flow between the two programs as a result of differences in cable data. Your length estimate for the cable will have a much bigger impact.
Remember there is ambient temperature and ultimate operating temperature, but there is also the reference temperature at which the conductor resistance is based.Last part of your first paragraph, are you stating the base parameters for the operating temp of the conductors are 75C & 90C?
JDRemember there is ambient temperature and ultimate operating temperature, but there is also the reference temperature at which the conductor resistance is based.
I have never seen power study software assume, as standard, conductors were operating at the maximum insulation temperature rating.
Perhaps more accurately stated as, 75C is assumed, unless a different temperature column applies.Does this not result in the cable is operating at 100%?
Software that wont allow MFG cable data assumes everybody complies with adopted standards.I would trust EasyPower more than SKM
The point is that all conductors of similar material and construction have basically the same electrical characteristics. This is determined by physics, not standards. The idea that #1/0 copper THHN from one manufacturer will have consistently different electrical characteristics from another manufacturer's similar cable just isn't realistic.Software that wont allow MFG cable data assumes everybody complies with adopted standards.
Are we in agreement that if you select the NEC library…the base starting point is 30C ambient and 75C conductor temperature?The point is that all conductors of similar material and construction have basically the same electrical characteristics. This is determined by physics, not standards. The idea that #1/0 copper THHN from one manufacturer will have consistently different electrical characteristics from another manufacturer's similar cable just isn't realistic.
Regarding the conductor temperature, as others noted, it is important to distinguish between ambient temperature and actual conductor temperature. The conductor temp will always be an educated guess or an assumption. The 75 deg C default can be changed for any cable. For short circuit calcs, the maximum current would occur at a very low temperature. For voltage drop calcs, the worst case is a fully loaded cable. During short circuits, the conductor temperature is not a constant but is rapidly increasing. So there are a lot of simplifying assumptions required regardless of how the calculation is done.
Profit determines material characteristics, not physics.This is determined by physics, not standards.
 
				