cable in conduit cable end seals
Wire-Smith
United States
what do you all use for end sealing cables, crouse hinds epoxy TSC? it isn't clearly labelled for this. what else is available?
i'm talking about when you run cable capable of transmitting gases in rigid, don't open the jacket in the seal off but seal the cable end in the enclosure where it terminates.
Dale001289
Georgia
If you were running ONLY multiconductor cable such as TC-ER or MC-HL (no conduit) you could use the TSC Epoxy Sealing compound along with a TMCX connector. But since the cable is routed within conduit, I believe you'll to have to use a conduit seal - such as EYS - open the jacket/separate the conductors and apply Chico compound.
Wire-Smith
United States
i disagree 501.15(D)(2) exception
cable w/ gas/vapor-tight sheath
Wire-Smith
United States
“Approved“ and “Approved Means” are not the same thing -
110.2 Approval. "the conductors and equipment required or permitted by this code shall be acceptable only if approved.
informational note. see... definitions of approved....."
once again, code reference please. i don't subscribe to dales electrical code just NEC
means
mēnz/
noun
[COLOR=#878787 !important][/COLOR]
  • 1.
    an action or system by which a result is brought about; a method.
put the two together and what do you have?
Dale001289
Georgia
are you thinking of listed? its different
The sealant must be explosion proof vs nonexplosion proof or simply “minimizing gases “ such as duct seal - it must be listed or labeled. Once it has been listed by an approved means it can then be approved the AHJ
Wire-Smith
United States
code reference please, not everything we use is listed, by what u r saying every electrical installation is in violation right now
Wire-Smith
United States
TSC is listed for explosion-proof seals
and no seal completely seals out gases, all of them only minimize
why the h*** do you think the code allows this?
Wire-Smith
United States
Exactly TSC is used with cable seals - why don’t you try reading from the beginning post pretty please
why don't you try reading the code book?
i agree tsc is for cable seals, always thought that. this post provides no good argument or information