I am having a fruitless argument with the electrical engineers in my department over conductors and cables for Class 1 Div 1 installation (they are designing a large ethane cracking plant). I'm an electrician who knows the NEC (passed both the exam for electrician years ago and the BOCA electrical inspectors exams) and have done countless XP installations in manufacturing plants and tank farms. I was also a factory rep for a while for OZ Gedney, Crouse Hinds and Carol Cable. Per the wording of Section 501.10(A)(1)(a) as long as you have a proper threaded conduit installation (with all the requisite seals and fittings) you can use ANY conductor or cable installed within that raceway. In fact we most often pulled THHN and blue hose in our raceway systems in classified locations. I told them that you could technically pull Romex in the conduit system if the plant specs allowed it.
But these engineers seem to think there has to be some explicit wording in the NEC stating that cables that will be wholly contained within a conduit system do not need to be explicitly "approved" for Class 1 Div 1. They confuse the sections in 501.10 describing the limited cable types for EXPOSED cabling installations with those cables also being required when enclosed in a conduit system. So they think that the only cables that they can pull in conduit in C1D1 areas are those called out for exposed cable installation. Yep, try to pull MI cable in rigid conduit, guys, I dare ya.
I've provided them with a couple of answers from this forum supporting my understanding but they keep asking "where does it say this is OK in the NEC?" They will not accept my explanation that, by default, if you install an= C1D1 approved raceway system you can install ANY type of cable in it that would meet standards in the rest of the plant outside the classified area.
Can anyone offer a Code reference that can help me convince these guys what those of us who install these systems have always known?
But these engineers seem to think there has to be some explicit wording in the NEC stating that cables that will be wholly contained within a conduit system do not need to be explicitly "approved" for Class 1 Div 1. They confuse the sections in 501.10 describing the limited cable types for EXPOSED cabling installations with those cables also being required when enclosed in a conduit system. So they think that the only cables that they can pull in conduit in C1D1 areas are those called out for exposed cable installation. Yep, try to pull MI cable in rigid conduit, guys, I dare ya.
I've provided them with a couple of answers from this forum supporting my understanding but they keep asking "where does it say this is OK in the NEC?" They will not accept my explanation that, by default, if you install an= C1D1 approved raceway system you can install ANY type of cable in it that would meet standards in the rest of the plant outside the classified area.
Can anyone offer a Code reference that can help me convince these guys what those of us who install these systems have always known?