Hello,

I have a new cable tray and need to get cables from existing cable tray into the new one. The new cable tray is perpendicular to the old one. Old cable tray stops when it reaches the new cable tray. Both trays are at the same elevation and i can't change elevation.

Do i need to get a cable tray "Tee" or can cables be routed from the existing cable tray over the new cable tray side rail (6")?

I coudn't find any publications preventing cables from being routed over the cable tray side rails...

Thanks,

Mike
 
mikelagoda said:
Do i need to get a cable tray "Tee" or can cables be routed from the existing cable tray over the new cable tray side rail (6")?

Most cable tray systems have "T" and other configs.
mikelagoda said:
I coudn't find any publications preventing cables from being routed over the cable tray side rails...
Not really a code issue as much as it is workmanship issue.

Thanks,

Mike[/quote]
 
RUWired said:
Most cable tray systems have "T" and other configs.

Not really a code issue as much as it is workmanship issue.

Thanks,

Mike
[/quote]

392.2 Definition.
Cable Tray System.​
A unit or assembly of units or sections
and associated fittings forming a structural system used to
securely fasten or support cables and raceways.

392.6 Installation.
(A) Complete System.​
Cable trays shall be installed as a
complete system. Field bends or modifications shall be so
made that the electrical continuity of the cable tray system
and support for the cables is maintained. Cable tray systems
shall be permitted to have mechanically discontinuous segments
between cable tray runs or between cable tray runs
and equipment.

 


392.6 Installation.​

(A) Complete System.

Cable trays shall be installed as a


complete system. Field bends or modifications shall be so
made that the electrical continuity of the cable tray system
and support for the cables is maintained. Cable tray systems
shall be permitted to have mechanically discontinuous segments
between cable tray runs or between cable tray runs
and equipment.​
[/quote]

I agree there allowed to be discontinous, but he was saying that he wanted to butt into the side rail of the tray. Not very professional IMO. I can see flowing off the end and onto another, but not into the side rail when they make fittings for that use.
 