I have a question regarding cable insulation rating.
To provide you with a background, we are tapping the iso-phase bus duct to power up an Auxiliary Bank for a steam turbine unit. The nominal voltage rating of this bus is 13.8kV; generator output is 13.8kV, and GSU xfmr is rated 13.8kV-230kV. The BOP design and construction company who built this unit installed medium voltage cable rated at 25kV, 133% insulation when tapping the iso-phase to the aux bank high side. Unfortunately, they installed a conduit that just the minimum size of what was needed, and we have come to a point where we need to up-size the cable.
My proposal is the following: instead of going with the same insulated-rated cable and having to install new conduit, downsize to 15kV, 133% insulated cable. This way, the overall insulation thickness of the cable is reduced and we can up the conductor size while still remaining within NEC fill requirements. In addition, this cable is readily stocked by Okonite (a cable mfr). Compared to this, 25kV rated cable (100% or 133% insulated cable) requires minimum order of 3000 feet and a 12 week lead time.
A plant electrician says we cannot do this due to the swings from the generator and grid-side. But I have dug up metering data from the past 2+ years that shows the max voltage occurrence that has ever happened on the iso-phase bus to be 14.65kV. In addition, I believe that the 133% insulation level will also provide plenty of added protection in case of potential faults, future voltage swings, etc.
Am I missing anything here? Is there a reason why the BOP contractor decided to go with 25kV @ 133% insulated cable? Is there any counter argument anyone can provide on why I cannot use 15kV @ 133% insulated cable for this 13.8kV system?
My suspicion of why this cable (i.e. 25kV @ 133%) was installed in the first place is because another unit built by the same contractor at the same has its' iso-phase bus rating of 18kV. The BOP contractor had to buy 25kV rated cable in bulk (cable manufacturers require minimum orders of 3000' as stated above) for this unit so they decided to use it for this other 13.8kV system instead of wasting the 25kV bulk-ordered cable. I haven't been able to confirm this with the BOP contractor since they built these units before my time at the plant.
I appreciate any help you guys can provide. Please let me know if you have any questions.
I have a question regarding cable insulation rating.
To provide you with a background, we are tapping the iso-phase bus duct to power up an Auxiliary Bank for a steam turbine unit. The nominal voltage rating of this bus is 13.8kV; generator output is 13.8kV, and GSU xfmr is rated 13.8kV-230kV. The BOP design and construction company who built this unit installed medium voltage cable rated at 25kV, 133% insulation when tapping the iso-phase to the aux bank high side. Unfortunately, they installed a conduit that just the minimum size of what was needed, and we have come to a point where we need to up-size the cable.
My proposal is the following: instead of going with the same insulated-rated cable and having to install new conduit, downsize to 15kV, 133% insulated cable. This way, the overall insulation thickness of the cable is reduced and we can up the conductor size while still remaining within NEC fill requirements. In addition, this cable is readily stocked by Okonite (a cable mfr). Compared to this, 25kV rated cable (100% or 133% insulated cable) requires minimum order of 3000 feet and a 12 week lead time.
A plant electrician says we cannot do this due to the swings from the generator and grid-side. But I have dug up metering data from the past 2+ years that shows the max voltage occurrence that has ever happened on the iso-phase bus to be 14.65kV. In addition, I believe that the 133% insulation level will also provide plenty of added protection in case of potential faults, future voltage swings, etc.
Am I missing anything here? Is there a reason why the BOP contractor decided to go with 25kV @ 133% insulated cable? Is there any counter argument anyone can provide on why I cannot use 15kV @ 133% insulated cable for this 13.8kV system?
My suspicion of why this cable (i.e. 25kV @ 133%) was installed in the first place is because another unit built by the same contractor at the same has its' iso-phase bus rating of 18kV. The BOP contractor had to buy 25kV rated cable in bulk (cable manufacturers require minimum orders of 3000' as stated above) for this unit so they decided to use it for this other 13.8kV system instead of wasting the 25kV bulk-ordered cable. I haven't been able to confirm this with the BOP contractor since they built these units before my time at the plant.
I appreciate any help you guys can provide. Please let me know if you have any questions.