jdping2
Member
- Location
- Monterey ca
I have a customer that had a 50 hp 3 phase 480 volt deepwell installed, motor is 600 feet below grade, fed with 3/0 copper drop cables , all of which were installed by well contractor. There is an existing square d wellguard combination starter that controls the new deepwell, the starter has a pumpsaver unit in it which up until 3 weeks ago, the starter was feeding an adjacent well which is now being decommisioned. The well contractor brought in a rental generator to test the recently installed deepwell and ran the motor for about 3 hours - this was done without a starter or overload relay, straight connection from generator (200amp 3 pole 600 volt main breaker), I was surprised that they ran a new motor directly to the generator without a starter, although did not say anything to them. I was also expecting the breaker to trip which it did not ( what about inrush current ?).
Anyways, prior to integrating the new deep well motor into existing controller I performed a megger test of the new deepwell cables which are connected to new 50 hp 480 v deepwell motor on one end and not connected to anything topside, Fluke 1587 FC , 1000v test range and heres what I found - A to ground 0.0m @1vdc, B to ground 0.0m @ 1vdc, C to ground 2.2G @ 1047 vdc. Then I checked between phases A to B 0.0m @ 1 vdc, A to C 2.2G @ 1047 vdc, B to C 2.2G @ 1047 vdc.
I am embarrased to admit that I do not know how to interprit the phase to phase readings, It is clear to me that the phase to ground readings indicate that A and B phase are both shorted to ground , and that C phase is clear to ground. According to the well contractor, there are no start or run capacitors in the deepwell motor. Grundfos No 92530624 MMS6NST50 . after presenting the megger readings to the deepwell contractor, he has stated that they weill be removing the deepwell motor to fix the issues, my main question here is - should there be any resistance between phases? Its Killing me that I can not figure this one out......
Anyways, prior to integrating the new deep well motor into existing controller I performed a megger test of the new deepwell cables which are connected to new 50 hp 480 v deepwell motor on one end and not connected to anything topside, Fluke 1587 FC , 1000v test range and heres what I found - A to ground 0.0m @1vdc, B to ground 0.0m @ 1vdc, C to ground 2.2G @ 1047 vdc. Then I checked between phases A to B 0.0m @ 1 vdc, A to C 2.2G @ 1047 vdc, B to C 2.2G @ 1047 vdc.
I am embarrased to admit that I do not know how to interprit the phase to phase readings, It is clear to me that the phase to ground readings indicate that A and B phase are both shorted to ground , and that C phase is clear to ground. According to the well contractor, there are no start or run capacitors in the deepwell motor. Grundfos No 92530624 MMS6NST50 . after presenting the megger readings to the deepwell contractor, he has stated that they weill be removing the deepwell motor to fix the issues, my main question here is - should there be any resistance between phases? Its Killing me that I can not figure this one out......