Cable or wire in pier side trough containing water pipe

Status
Not open for further replies.

smfloyd

Member
Location
New Hampshire
Occupation
Engineer
There is a concrete trench on the deck of a water side pier that contains a 4 inch diameter water pipe. The trench is about 2 feet wide by 18 inches deep. It is desired to run 480 VAC 3 phase in this same trench. We want to run either G-GC CABLE or XHHW-2 wire. Question, do either of these need to be in their own conduit/raceway?
My concern is NEC 300.8
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The cable spec states "Not for use as permanent building wiring". It seems like a very robust wiring method, for "flexible, portable, and extra-hard usage applications"
I would use PVC conduit with expansion couplings and XHHW-2 conductor
 

smfloyd

Member
Location
New Hampshire
Occupation
Engineer
Thanks Tom, the electrician/contractor just wants to bundle the 480 VAC 3 phase XHHW-2 and lay it in the trench. I think conduit is required/good idea. I’m trying to find a NEC code requirement for the conduit.
 

tthh

Senior Member
Location
Denver
Occupation
Retired Engineer
Thanks Tom, the electrician/contractor just wants to bundle the 480 VAC 3 phase XHHW-2 and lay it in the trench. I think conduit is required/good idea. I’m trying to find a NEC code requirement for the conduit.
Can't make sense to lay XHHW-2 in a trench with a water pipe. What about the poor plumber who comes along in 5 years? Makes no sense.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Thanks Tom, the electrician/contractor just wants to bundle the 480 VAC 3 phase XHHW-2 and lay it in the trench. I think conduit is required/good idea. I’m trying to find a NEC code requirement for the conduit.
No conduit needEd if the trench is a chapter 3 wiring method.
just ask your electrician for the concrete trench article number
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
the electrician/contractor just wants to bundle the 480 VAC 3 phase XHHW-2 and lay it in the trench. I think conduit is required/good idea. I’m trying to find a NEC code requirement for the conduit.
As others have pointed out 300.3 and I'll add 300.2:
Code:
300.2 Limitations.
(A) Voltage. Wiring methods specified in Chapter 3 shall be
used for 1000 volts, nominal, or less where not specifically limited in some section of Chapter 3.

Code:
300.3 Conductors.
(A) Single Conductors. Single conductors specified in
Table 310.104(A) shall only be installed where part of a recognized wiring method of Chapter 3.

There is only one exception:
Exception: Individual conductors shall be permitted where
installed as separate overhead conductors in accordance
with 225.6.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Since the application under discussion is on a pier, isn't there something in Chapter 5 that bears on this question? Maybe that would allow the G cable laid in the trench?

Edit: looks like 555.13 would be applicable, and cable would only be a possibility if the trench is on the underside of the pier or "flexibility is necessary as on piers composed of floating sections"

Cheers, Wayne
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
There is a concrete trench on the deck of a water side pier that contains a 4 inch diameter water pipe. The trench is about 2 feet wide by 18 inches deep. It is desired to run 480 VAC 3 phase in this same trench. We want to run either G-GC CABLE or XHHW-2 wire. Question, do either of these need to be in their own conduit/raceway?
My concern is NEC 300.8
Concrete trench on a deck of a pier? Or is this a jetty? How are you getting a "concrete trench" into a pier? What sort of covering would be on this "concrete trench"?
XHHW-2 is not listed to be installed "unprotected", it might contain additional listing for direct burial and thus protection by burial. But a concrete trench is not direct buried, but in this suggested application "concrete trench" is being used as a raceway. If this "trench" is going to contain "foreign" (non electrical) installation, it would seem you can't also count it as a raceway thus any electrical installation would require it's own raceway within the "trench". Anybody considering installing plumbing through your electrical enclosures or raceways?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
IMO, Since it's a pier, Art 555 will allow the G Cable without conduit. Installations such as that have been approved locally (doesn;t mean they are correct but our AHJs approved)
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
IMO, Since it's a pier, Art 555 will allow the G Cable without conduit.
555.13(A)(2) allows certain "portable power cables" in two cases:

(1) As permanent wiring on the underside of piers (floating or fixed)
(2) Where flexibility is necessary as on piers composed of floating sections

I don't see how a trench in the deck of a pier meets (1)? I guess you could interpret "underside" to mean "anywhere below the walking surface".

Cheers, Wayne
 