I'm involved with a project in which we're trying to re-use existing cabling as much as possible. Long story short, there's a cabinet that contains a wye-delta starter for a 200hp motor. The motor requires a tremendous amount of torque to start up. The wye-delta starter timer is set to switch over to delta after 7 minutes. I'm wanting to rip out the wye-delta starter and install a soft start. We've used these soft starts on identical motors before, so I know that using the soft-start, it draws about 575A for 6-7 minutes. However, I found that the old wye-delta is being fed with single 300kcmil cabling. NEC code says 300's are good for a little over 300A. My question is if I re-use this cable with the soft start it will be overloaded for 6-7 minutes by almost 300A. Can cables handle that amount of overload, for that amount of time? I know best-case scenario I re-pull new, but that would require an outage, which is a big ordeal in the plant I work in.