EricPeterson
Member
- Location
- 78260
- Occupation
- Design Engineer
OK, looks like I might have found somewhere with some resident experts!
At work we're conducting an ongoing project to transition all of our oilfield equipment wiring products to CSA certification. These are engine management, compressor, control system, and sensor harnesses mounted to everything from small pumps to heavy lift palletized gas compressor arrays. We've been successful clearing certification for harnesses residing entirely within the Class 1 Div 2 volume but are now faced with a new challenge. One of our cables originating within the hazardous zone passes completely outside of the area and needs to break out to several different arrays of sensors, none of which are designed for hazardous environments themselves and all of which are fitted with automotive style pigtails with automotive style plastic single-snap connectors.
The origination inside the hazardous zone is a modified MS 5015 style threaded, hermetically sealed connector/backshell assembly. The cable itself is TC-ER with two extra layers of protection, the first an additional layer of PVC insulation, and the second a braided abrasion resistant oversheath. This style of assembly satisfies all the conductor separation and insulation requirements for certification and is working well through CSA and for our customers when located completely inside the hazardous area.
Some, but not all, of the circuits in this new single TC-ER cable carry incendive signals.
Now that we need to connect to sensor arrays outside the hazardous area, what do we do? How do we transition from the cable for the hazardous area to the pigtails to the automotive style connectors?
Opinions have included:
(1) Not possible. Once incendive protection required, always incendive protection required, regardless of the environment. The sensors outside the zone need to be upgraded to Class 1 Div II units, and if they're not available, existing units need to be modified, rewired, and separately qualifed/certified.
(2) The style and construction of the sensor cable needs to remain fully certifiable, using appropriate materials and connectors, and at the other end, the sensors can be modified to wire into mating connectors.
(3) The style and construction of the sensor cable needs to remain fully certifiable, using appropriate materials and connectors, and at the other end, needs to plug into a sealed junction box entirely outside the hazardous area. The junction box presents breakouts for cables running to the sensors, which remain stock.
(4) The TC-ER cables need to run all the way to the automotive style connector mates maintaining all standards. Some sort of effort needs to be made to seal the back end of the automotive style connectors to the TC-ER cables. Some sort of "needs a tool" protective device needs to be applied to each connector assembly at each sensor pigtail. The sensor pigtails don't need to be modified.
(5) Full protection of the TC-ER cable and oversheaths need only run some prudent distance outside the Class I Div 2 zone. Once safely outside the hazardous environment, the outer layer of the TC-ER cable insulation can be removed and the individual circuits and twisted sets can be broken out and routed to mating connectors for the sensor pigtails with industrial-automotive level wear protection. No "needs a tool" locking device is required for the connector pairs, which will unsnap from one another with a thumb press on a plastic tab.
I haven't identified a section that specifically addresses this case. Where do I look or what's correct?
At work we're conducting an ongoing project to transition all of our oilfield equipment wiring products to CSA certification. These are engine management, compressor, control system, and sensor harnesses mounted to everything from small pumps to heavy lift palletized gas compressor arrays. We've been successful clearing certification for harnesses residing entirely within the Class 1 Div 2 volume but are now faced with a new challenge. One of our cables originating within the hazardous zone passes completely outside of the area and needs to break out to several different arrays of sensors, none of which are designed for hazardous environments themselves and all of which are fitted with automotive style pigtails with automotive style plastic single-snap connectors.
The origination inside the hazardous zone is a modified MS 5015 style threaded, hermetically sealed connector/backshell assembly. The cable itself is TC-ER with two extra layers of protection, the first an additional layer of PVC insulation, and the second a braided abrasion resistant oversheath. This style of assembly satisfies all the conductor separation and insulation requirements for certification and is working well through CSA and for our customers when located completely inside the hazardous area.
Some, but not all, of the circuits in this new single TC-ER cable carry incendive signals.
Now that we need to connect to sensor arrays outside the hazardous area, what do we do? How do we transition from the cable for the hazardous area to the pigtails to the automotive style connectors?
Opinions have included:
(1) Not possible. Once incendive protection required, always incendive protection required, regardless of the environment. The sensors outside the zone need to be upgraded to Class 1 Div II units, and if they're not available, existing units need to be modified, rewired, and separately qualifed/certified.
(2) The style and construction of the sensor cable needs to remain fully certifiable, using appropriate materials and connectors, and at the other end, the sensors can be modified to wire into mating connectors.
(3) The style and construction of the sensor cable needs to remain fully certifiable, using appropriate materials and connectors, and at the other end, needs to plug into a sealed junction box entirely outside the hazardous area. The junction box presents breakouts for cables running to the sensors, which remain stock.
(4) The TC-ER cables need to run all the way to the automotive style connector mates maintaining all standards. Some sort of effort needs to be made to seal the back end of the automotive style connectors to the TC-ER cables. Some sort of "needs a tool" protective device needs to be applied to each connector assembly at each sensor pigtail. The sensor pigtails don't need to be modified.
(5) Full protection of the TC-ER cable and oversheaths need only run some prudent distance outside the Class I Div 2 zone. Once safely outside the hazardous environment, the outer layer of the TC-ER cable insulation can be removed and the individual circuits and twisted sets can be broken out and routed to mating connectors for the sensor pigtails with industrial-automotive level wear protection. No "needs a tool" locking device is required for the connector pairs, which will unsnap from one another with a thumb press on a plastic tab.
I haven't identified a section that specifically addresses this case. Where do I look or what's correct?