501.15(E)(1)
(1) Terminations. "Cables entering enclosures that are required to be explosionproof shall be sealed at the point of entrance. The sealing fitting shall comply with 501.15(B)(1) or be explosionproof. Multiconductor or optical multifiber cables with a gas/vaportight continuous sheath capable of transmitting gases or vapors through the cable core that are installed in Division 2 location shall be sealed with a listed fitting after the jacket and any other coverings have been removed, so that the sealing compound can surround each individual insulated conductor or optical fiber tube in such a manner as to minimize the passage of gases and vapors…"
My understanding is, third sentence (red letters) simply qualifies cable type as it applies to explosionproof enclosures - only. Some interpret this to mean ALL multiconductors must be sealed, regardless of type termination/enclosure in Class I, Division 2 locations.
Comments?
(1) Terminations. "Cables entering enclosures that are required to be explosionproof shall be sealed at the point of entrance. The sealing fitting shall comply with 501.15(B)(1) or be explosionproof. Multiconductor or optical multifiber cables with a gas/vaportight continuous sheath capable of transmitting gases or vapors through the cable core that are installed in Division 2 location shall be sealed with a listed fitting after the jacket and any other coverings have been removed, so that the sealing compound can surround each individual insulated conductor or optical fiber tube in such a manner as to minimize the passage of gases and vapors…"
My understanding is, third sentence (red letters) simply qualifies cable type as it applies to explosionproof enclosures - only. Some interpret this to mean ALL multiconductors must be sealed, regardless of type termination/enclosure in Class I, Division 2 locations.
Comments?