Andy Sherrill
Member
I work in a chemical plant and we are struggling with the NEC Cable Seal requirements. We use a lot of multiconductor cable in conduit. Our electric rooms have supply fans to insure the rooms operate at a slight positive pressure to prevent dust and chemicals from entering the electric rooms. However, this is not verified by pressure switches.
Just to make sure I am understanding the code correctly, I interpret 501.15(D)(1) as requiring teh terminations of the cable to be sealed. I interpret 501.15(D)(2) & (3) as different methods of sealing the cables at the above listed terminations. I interpret 501.15(E) as being similar requirements for Div. 2 areas where the enclosure is required to be explosion proof.
Is my understanding correct?
Our electricians are telling me it is virtually impossible to make sure they get the end of the multiconductor cable stripped back to teh conduit seal for the enclosure and make sure they get the individual conductors separated all in this one seal. I am attempting to use the exception under 501.15(D)(2) and find an "approved" means to seal the end of the multiconductor cable inside the enclosure and treat the cable as a single conductor for the conduit seal.
I understand the "approved" can mean different things. We do not have an outside AHJ. We have our own electrical inspector, so I guess approved means a method our company approves.
Does anyone know of a sealing kit that works well for this type of multiconductor cable?
Also, the actual code and the explaination in the Handbook do not seem to agree completely on the exception under 501.15(D)(1). The code says the shielding does not have to be removed. The Handbook explaination says the outer sheathing does not have to be removed. I have read different posts that discuss the problems with sealing material against the shield. What is the generally accepted practice for this exception?
Sorry for the long post.....very difficult subject to describe adequately!
Just to make sure I am understanding the code correctly, I interpret 501.15(D)(1) as requiring teh terminations of the cable to be sealed. I interpret 501.15(D)(2) & (3) as different methods of sealing the cables at the above listed terminations. I interpret 501.15(E) as being similar requirements for Div. 2 areas where the enclosure is required to be explosion proof.
Is my understanding correct?
Our electricians are telling me it is virtually impossible to make sure they get the end of the multiconductor cable stripped back to teh conduit seal for the enclosure and make sure they get the individual conductors separated all in this one seal. I am attempting to use the exception under 501.15(D)(2) and find an "approved" means to seal the end of the multiconductor cable inside the enclosure and treat the cable as a single conductor for the conduit seal.
I understand the "approved" can mean different things. We do not have an outside AHJ. We have our own electrical inspector, so I guess approved means a method our company approves.
Does anyone know of a sealing kit that works well for this type of multiconductor cable?
Also, the actual code and the explaination in the Handbook do not seem to agree completely on the exception under 501.15(D)(1). The code says the shielding does not have to be removed. The Handbook explaination says the outer sheathing does not have to be removed. I have read different posts that discuss the problems with sealing material against the shield. What is the generally accepted practice for this exception?
Sorry for the long post.....very difficult subject to describe adequately!