Re: cable selection
Is there such thing as a 40A panel? Asumming a few things due, I am supposing since this is a feeder it will either be 240V or 480V. I am also assuming 5% voltage drop and a K value of 12.9 for copper conductors.
At 240V, #3 AWG will be sufficent for a 40A load
At 480V, #6 AWG will be sufficent for a 40A load