vkali
New member
- Papua New Guinea
What cable size is suitable for a 550kVA diesel generator rated at 400V, 794A and 50Hz? How do I determine cable sizes for such installations?
XPLE is becoming more common.In the absence or more detailed information, I would suggest that if UK type armoured cable is to be used, that two cables each 4 core 240mm be used in parralel.
That size cable is, normal ambient temperatures, suitable for from 409 amps to 445 amps depending on how installed.
Article 445 of the National Electrical Code contains rules for generators. The ampacity of the conductors from the generator terminals to the first distribution device containing overcurrent protection shall not be less than 115 percent of the nameplate current rating of the generator.