I have an 800A 480V distribution panel that I must size a feeder for.
The maximum continuous current permitted per the NEC for the CB would be 640A. (CB not listed for continuous duty)
My solution would be to size the feeder for 800A which is 125% of the maximum continuous load.
This would be 3 sets of 300KCMIL CU per phase with 3 #4AWG CU grounds.
The cable ampacity is based on the 75 deg C rating, which is what most lugs are listed at.
Am I correct?