NOPete
Member
- Location
- Terrytown, LA
I have a distribution panel feeding a 150kVA 480 to 208/120 transformer. Engineering has designated a 300-amp breaker in the DP for the power supply. They have also designated a 3/C #4/0 cable for the primary from the breaker to the transformer.
My concern is that the #4/0 cable is only rated for 240 amps (@ 75C), and is landed under a 300-amp breaker.
Is there ANY NEC Code reference that allows a cable to be landed under a breaker which has a higher amp rating than the cable...???
My concern is that the #4/0 cable is only rated for 240 amps (@ 75C), and is landed under a 300-amp breaker.
Is there ANY NEC Code reference that allows a cable to be landed under a breaker which has a higher amp rating than the cable...???