Hi!
As per AS/NZS 3000:2018, a cable is protected if Iz≥In and I2≤1.45xIz, where In is the MCCB nominal current, Iz is the derated current capacity of the cable and I2 is the effective tripping current of the MCCB.
What I don’t understand is the I2≤1.45xIz part. As per AS/NZS 60898, 1.45xIn was tested to trip circuit breakers within a time <2hr for In>63A. So for currents below this level the MCCB may not trip? In that case, shouldn't the cable be sized for >1.45xIn?
The I2≤1.45xIz seems to imply that if my I2=100A (effective tripping time is 100A), then a cable with derated capacity of 70A is perfectly okay… but for any loading between 70A and 100A in that cable my MCCB may never trip and my cable will burn eventually?
I'm looking to use a TemBreak PRO with a +5% to +20 tolerance band, so my I2 would be 1.2xIn as a worst case I assume, not 1.45xIn.
I have a client asking for a 630A MCCB to feed a 630A switchboard. If I have a 600A load with the 630A MCCB and a cable derated for 690A we pass all items, but if someone keeps adding loads to the switchboard until I have 720A then my MCCB may never trip as the effective tripping current is 630x1.2=756A and my cable will slowly burn? So do I size my cable for >756A?
Thanks!
As per AS/NZS 3000:2018, a cable is protected if Iz≥In and I2≤1.45xIz, where In is the MCCB nominal current, Iz is the derated current capacity of the cable and I2 is the effective tripping current of the MCCB.
What I don’t understand is the I2≤1.45xIz part. As per AS/NZS 60898, 1.45xIn was tested to trip circuit breakers within a time <2hr for In>63A. So for currents below this level the MCCB may not trip? In that case, shouldn't the cable be sized for >1.45xIn?
The I2≤1.45xIz seems to imply that if my I2=100A (effective tripping time is 100A), then a cable with derated capacity of 70A is perfectly okay… but for any loading between 70A and 100A in that cable my MCCB may never trip and my cable will burn eventually?
I'm looking to use a TemBreak PRO with a +5% to +20 tolerance band, so my I2 would be 1.2xIn as a worst case I assume, not 1.45xIn.
I have a client asking for a 630A MCCB to feed a 630A switchboard. If I have a 600A load with the 630A MCCB and a cable derated for 690A we pass all items, but if someone keeps adding loads to the switchboard until I have 720A then my MCCB may never trip as the effective tripping current is 630x1.2=756A and my cable will slowly burn? So do I size my cable for >756A?
Thanks!