Can anyone give me some instructions on how to perfom Zero Sequance Impedance Test on an HV cable and what test equipment I would have to use, any help appreciated.
Zero Sequence Impedance is the impedance to ground so if you want to measure the impedance to ground you want to megger the cable or perform a power factor test.
Never heard of it. Where are you getting that from? MV/HV cables should be tested by one of 3 methods.
1. Tan Delta
2. Partial Discharge
3. VLF
Zog,
How about DC Hi-Pot test?
We have done the DC hipot test arguement here several times. But in case you missed it, MV/HV serviced aged (5 years) cables should not be DC hipot tested per IEEE, ANSI, NETA, and ICEA cable testing standards. It is considered a destructive test and has proven to shorten the life expectantcy of the cable.
Zog,
I must have missed it..Can you provide me the link to that discussion?