Jeff Q
Member
- Location
- Wisconsin, USA
- Occupation
- Electrical engineer
We are using 12 sets per phase including Neutral of 350 KCMIL cable on a 30" ladder type uncovered cable tray, need an amp rating more than 4000A to meet the spec.
350KCMIL =505A ampacity X12 sets =6060A . if multiplied by Cable tray Adjustment factor 0.65 per 392.80(A)(2)(b) we get 3939A and multiplied again by the 75c ambient temperature which is 0.88 per 310.15(B)(2)(a). Which gives us 3466A not meeting the 4000A criteria.
Can cable tray adjustment factor be 0.80 instead of 0.65 if we maintain a distance of 2.15*1.08(Cable OD)=2.32" between the bundle ? If so , The calculation looks like this. 505Ax12=6060A, x0.80(cable tray adjustment factor)= 4848A and then multiplied by ambient temp derating factor X 0.88=4226A meeting the criteria.
Please let me know if this is acceptable to get a free air rating of 80% if 2.322" of distance is maintained between each bundle.
350KCMIL =505A ampacity X12 sets =6060A . if multiplied by Cable tray Adjustment factor 0.65 per 392.80(A)(2)(b) we get 3939A and multiplied again by the 75c ambient temperature which is 0.88 per 310.15(B)(2)(a). Which gives us 3466A not meeting the 4000A criteria.
Can cable tray adjustment factor be 0.80 instead of 0.65 if we maintain a distance of 2.15*1.08(Cable OD)=2.32" between the bundle ? If so , The calculation looks like this. 505Ax12=6060A, x0.80(cable tray adjustment factor)= 4848A and then multiplied by ambient temp derating factor X 0.88=4226A meeting the criteria.
Please let me know if this is acceptable to get a free air rating of 80% if 2.322" of distance is maintained between each bundle.