I have been trying to understand cable tray and ampacity better. Could someone confirm or dispute my opinion. Lets use 3-single 500kcm conductors in cable tray with reduced ground, ventilated cable tray.
Normal table 310.16 @75 degrees 380amps
Cable tray flat single layer no separation 310.17 x 65%=403amps
Triangle shape with 2.15 space 310.20=496amps
Each cable flat 1 cable space in between 310.17=620amps
Normal table 310.16 @75 degrees 380amps
Cable tray flat single layer no separation 310.17 x 65%=403amps
Triangle shape with 2.15 space 310.20=496amps
Each cable flat 1 cable space in between 310.17=620amps