So NEC section 392.80(A)(1)(a) basically says go ahead and fill a cable tray with multi-conductor cable.
derating is only required if you exceed 3 current carrying conductors per cable.
Meanwhile ICEA P-54-440 has mandatory derating based on tray fill.
So question is when to use one vs. the other, if anyone has any experience with this.
Appreciate it