Cable Tray Ampacity - NEC or ICEA P-54-440 (NEMA WC 51)

Status
Not open for further replies.

designer82

Senior Member
Location
Boston
So NEC section 392.80(A)(1)(a) basically says go ahead and fill a cable tray with multi-conductor cable.
derating is only required if you exceed 3 current carrying conductors per cable.

Meanwhile ICEA P-54-440 has mandatory derating based on tray fill.

So question is when to use one vs. the other, if anyone has any experience with this.

Appreciate it
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
So NEC section 392.80(A)(1)(a) basically says go ahead and fill a cable tray with multi-conductor cable.
derating is only required if you exceed 3 current carrying conductors per cable.

Meanwhile ICEA P-54-440 has mandatory derating based on tray fill.

So question is when to use one vs. the other, if anyone has any experience with this.

Appreciate it
have you looked at 392.22?

In any case, ICEA standards are not enforceable unless it is a contractual matter.
 