It is my understanding that if the cable tray is not serving as an equipment grounding conductor, it should be bonded from the ground bus bar in the gear of the cables that are routed in the cable tray to the side wall of the cable tray, and not to the grounding electrode system.
However, the image below (from B-Line manual) is confusing me a bit. Why is the bonding jumper from the MCC to the cable tray necessary? If there was a line-ground fault anywhere in the cable tray, the fault has a path to travel back to the source on the bonding jumper in the switchgear.
Why is there a jumper between the ground bus of the MCC and the building steel? The building steel should be bonded to grounding electrodes, the GEC, or switchgear enclosure per 250.104(C).