sparky8too
Member
I am looking for clarification in regards to cable tray bonding to building steel and earth. NEMA VE 2 states the 60' rule if the supports of the tray are isolated. If the tray is supported through metallic support systems than the 60' rule does not apply. NEC 250.96 requires the tray to be bonded where necessary. On a 400' run of tray what would "where necessary" imply? Thanks