Re: CABLE TRAY INSTALLATION
Section 392.4 only talks about cable tray not being used in hoistways or in areas subject to severe physical damage. This section refers to areas where the cable that is being supported by tray is acceptable, but not where tray can be used. You can look in B-Line's website for technical article CT02man for this information.