Why would 392.60(C) refer to 250.102 and not 250.122 when sizing bonding jumpers ????????????????????????????????????????????/
It does not seem like it matters much since 250.102(D) refers you to 250.122 fro equipment bonding jumpers.
It is possible that the installation would require a supply side bonding jumper and not an EGC. The reference to 250.102 covers both cases.Why would 392.60(C) refer to 250.102 and not 250.122 when sizing bonding jumpers ????????????????????????????????????????????/
Can a ssbj be anything other than a wire type conductor?It is possible that the installation would require a supply side bonding jumper and not an EGC. The reference to 250.102 covers both cases.
Yes, it can be a non-flexible metal raceway. That does not include cable tray, but it is is often used as such.Can a ssbj be anything other than a wire type conductor?