Currently working on a project where we have an electrical building with an overhead cable tray (BLine Ladder Type) with no covers. Currently the cable tray has a mixture of cables larger than 4/0 & smaller than 4/0 in the tray which has been properly sized per the 2023 NFPA 70, section 392.22(A)(1)(c).
The issue is that the 3rd Party inspector (Authority Having Jurisdiction), for the building manufacturer is trying to state that the multiconductor feeder cables that we have run in the tray between the 480V switchboard feeder breaker and the MLO of the Motor Control Center need to be derated per 2023 NFPA 70, section 310.15(C)(1).
It is clear to me that he is getting confused between the terms "Raceway" and "Cable Tray" as they are not the same device. He is stating the section in 310.15(C)(1) that says "Each current carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor" which would therefore lead him to believe that the 5 parallel sets of 3/C 500MCM w/Gnd cables would need to follow the ampacity rating of Table 310.16 (90C XHHW conductors) which we would also derate for ambient temperature Table 310.15(B)(1)(1). He however is stating that we need to also derate based on Table 310.15(C)(1) based on the number of current carrying conductors (He understands this to be 5 times 3 = 15 current carrying conductors because of the parrallel conductor statement in 310.15(C)(1)) This would require us to derate the 500MCM cable to 50% of its rated value in Table 310.16.
We are trying to explain to him that section 392.80(A)(1)(a) states you should only go to 310.15(C)(1) only for multiconductor cables with more than three current carrying conductors. None of the multiconductor power cables that we have include more than three current carrying conductors, only 3 Phase conductors and a Ground - No Neutral.
Furthermore, the section he is referencing also states that "Where conductors are installed in cable trays, 392.80 shall apply", NFPA 70 310.15(C)(1)(a), negating any of this information he has brought up regarding counting each parallel conductor as an individual current carrying conductor.
Thoughts??
The issue is that the 3rd Party inspector (Authority Having Jurisdiction), for the building manufacturer is trying to state that the multiconductor feeder cables that we have run in the tray between the 480V switchboard feeder breaker and the MLO of the Motor Control Center need to be derated per 2023 NFPA 70, section 310.15(C)(1).
It is clear to me that he is getting confused between the terms "Raceway" and "Cable Tray" as they are not the same device. He is stating the section in 310.15(C)(1) that says "Each current carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor" which would therefore lead him to believe that the 5 parallel sets of 3/C 500MCM w/Gnd cables would need to follow the ampacity rating of Table 310.16 (90C XHHW conductors) which we would also derate for ambient temperature Table 310.15(B)(1)(1). He however is stating that we need to also derate based on Table 310.15(C)(1) based on the number of current carrying conductors (He understands this to be 5 times 3 = 15 current carrying conductors because of the parrallel conductor statement in 310.15(C)(1)) This would require us to derate the 500MCM cable to 50% of its rated value in Table 310.16.
We are trying to explain to him that section 392.80(A)(1)(a) states you should only go to 310.15(C)(1) only for multiconductor cables with more than three current carrying conductors. None of the multiconductor power cables that we have include more than three current carrying conductors, only 3 Phase conductors and a Ground - No Neutral.
Furthermore, the section he is referencing also states that "Where conductors are installed in cable trays, 392.80 shall apply", NFPA 70 310.15(C)(1)(a), negating any of this information he has brought up regarding counting each parallel conductor as an individual current carrying conductor.
Thoughts??