I have 21, 3 phase 4 wire inverter output circuits (84 conductors total) to run in cable tray. The conductors will be 250 XHHW (CT use). My reading of 392.10(A)(2) is that I can have about 104 250 MCM conductors (.691 OD) in a 36 inch wide cable tray.

Questions:
1. Do you concur with the above?
2. These conductors will clearly not fit in a single row, but I am not seeing any guidance as to how they are to be grouped/layered. 300.3(B) requires grouping, but apparently only within the same tray, not specifically grouped in groups within the tray.
3. Say I have one conductor smaller than 250 MCM. It appears that I then use 392.10(A)(4) which cuts my max fill nearly in half, to sum of diameters not exceeding width of tray, seems odd is this correct?
 
Perhaps 392.22(B)(1)?

You can go up to 39in² according to Table.

.691² × pi ÷ 4 = 0.375in² per

... × 84 = 31.5in²

GTG.

Group by circuit.
 