Cable Tray Rungs Spacing

Status
Not open for further replies.

D!NNy

Senior Member
Location
San Luis Obispo
Can someone explain why 9" rung spacing is required per 392.10 for single conductor cables for sizes between 1/0 through 4/0? if this to avoid smaller conductors drooping (saging) between in the rungs, then why the code is not restricting with 9" rung spacing for multi conductor cables of sizes #10, #12, #8 etc which has less overall diameter less than #1/0?
 
Can someone explain why 9" rung spacing is required per 392.10 for single conductor cables for sizes between 1/0 through 4/0? if this to avoid smaller conductors drooping (saging) between in the rungs, then why the code is not restricting with 9" rung spacing for multi conductor cables of sizes #10, #12, #8 etc which has less overall diameter less than #1/0?

Cable tray design criteria is nuts. It is very difficult to understand any of the reasons, or find any consistency within the cable tray design flowchart.

There are also a lot of unanswered holes in cable tray design requirements. It may be due to the fact that it is a relatively new technology, and the code hasn't caught up with understanding all of what can happen with cable tray systems.
 
It could be that multi-conductor cables are considered more flexible. Or maybe its because they just don't weight as much.
 
It could be that multi-conductor cables are considered more flexible. Or maybe its because they just don't weight as much.

If multiconductor cables are more flexible (which they are), it would make me conclude that multiconductor cables require a closer rung spacing, for equivalent amount of total KCMIL within the conductor.

The way that weight affects the strength/stiffness of a conductor in a cable tray isn't as we are ordinarily used to. The stiffness is proportional to diameter^4, and the strength is proportional to diameter^3. Lineal weight is proportional to diameter^2. As the conductor grows, its "structural" ablity to span the gap improves.

Given a multiconductor cable with a total diameter that is less than an equivalent single conductor, it wouldn't make sense for it to span a larger gap. Unless we are talking about a metal clad cable, where the metal cladding helps it. Not so much for SER/SEU or other non-metal enclosed cable assemblies.
 