Cable Tray Sizing - mix of multi- and single-conductor

Status
Not open for further replies.
I have a condition with a mix of multi-conductor cables and single conductor cables in the same tray, including some single-conductor cables below 4/0. Section 392.22(A)(1) is titled "Ladder or Ventilated Cable Trays Containing Any Mixture of Cables", but its under the heading for Multiconductor cables, so I don't think this counts for a mix of multi- and single- cables. Do I calculate the required width for each cable type and add them together?

The other thing that's tripping me up is 392.22(B)(1)(d) says "where an of the single conductor cables are 4/0AWG or smaller, the sum of diameters of all single conductor sables shall not exceed the tray width". I have mostly larger cables, but a few 4/0 and smaller. Why does the presence of a couple smaller cables mean that all cables must follow that rule?

An example tray for my project is:
covered ladder style tray
(20) 400MCM XHHW-2
(12) 350MCM XHHW-2
(4) 300MCM XHHW-2
(12) 4/0 XHHW-2
(1) 1/0 THWN
(6) 4-Conductor #6 MC


I would be inclined to say:
- sum of conductor diameters for 4/0 and #6 MC cables is 7.4", so 8" is enough for this portion of cables.
- area of 250mcm and larger cables is 17 square inches. Per table 392.22(B)(1) col 1, 16" is enough for this portion of cables.
- the total tray then must be 8" + 16" = 24".

Does that make sense?
 
Approach it from this perspective: single-conductor cables are just multiconductor cables with one conductor. Use 392.22(A) only.
 
I guess that works. The factor -1.2Sd becomes a much larger number when you're talking about 4 single conductor cables rather than a 4/c MC cable. So that would be being conservative.

What about the funky issue of 392.22(B)(1)(d), saying that if any single conductor cables are 4/0 or smaller than the sum od diameters of all single conductor cables cannot exceed cable width? I don't get that one...
 
I guess that works. The factor -1.2Sd becomes a much larger number when you're talking about 4 single conductor cables rather than a 4/c MC cable. So that would be being conservative.

What about the funky issue of 392.22(B)(1)(d), saying that if any single conductor cables are 4/0 or smaller than the sum od diameters of all single conductor cables cannot exceed cable width? I don't get that one...
The general idea is to force one layer or grouped and spaced for conductors 1/0 and larger.
 